When Transitioning to SafeOp Third-Party EtherCAT® Slave Throws an Emergency Error
Updated Mar 31, 2025
When trying to go to SafeOp mode the ATEQ F620 Slave throws an emergency.
Emergency code: x400
Emergency data: DC 26 05 80 04
Capture the Wireshark log and see if you find error 0x8008.
It is a low-level application-layer error.
The error is indicating that the watchdog was set to zero by the master, while the slave expects it to be a different value. Solution is to add this line in the XML:
.../Eeprom>
<ESC>
<Reg0410>#x03E8</Reg0410>
</ESC>
The Register value 0410 indicates the watchdog timer and x03E8 simply a high value given to it instead of the 0 that NI EtherCAT master set.
The above steps are also relevant for the following slaves:
  • Sick MLG-2 Pro Light Screen
  • Sigmatek VBC 121
  • Hilscher CIFX 50-RE
  • Hilscher Gateway NT 151-RE-RE/+ML