The module might not show up for a variety of reasons. Below are possible causes, listed in order of probability and effort:
- You only need to download a configuration file to the module if you plan to use it as a master. Therefore, if you are using the PROFIBUS Slave module, or the Master/Slave module as a slave, you do not need to use Configurator.
- The C Series PROFIBUS module needs to be in slot 1 of the cRIO, with slot 2 empty, refer the manual. Please check to see if your cRIO slots are configured correctly.
- Confirm that the PROFIBUS module is powered with 24 VDC from a reliable external power supply.
- Install NI-VISA to the cRIO, if not already installed. See Install Software on Your CompactRIO Controller for more information.
- Confirm that the version of NI-VISA installed on the cRIO matches the version of NI-VISA installed on the PC.
- Make sure the VISA Remote Server is configured as described in Setting Up the CompactRIO PROFIBUS Module.
- The Master/Slave module might be in Autoslave mode. To switch the mode, follow the instructions in Why Can I Not Download a New Configuration to My C Series PROFIBUS Module?.
Note: After changing any part (hardware or software) of your setup, click
Search cRIO PB Devices in the Hardware Selection window of Configurator in order to refresh the hardware list.